RE: W6100 데이타 수신시 -119
by jisoon jung ·
안녕하세요,
통신은 Siemens PLC S7-1500(6ES7513-1AL02) 와 Modbus TCP로 교신 중인데 읽기에서 60개워드부터 문제가 발생합니다.
읽기개수(워드): 64 => get_rx_packet_size = -119 리턴이 됩니다.
읽기개수(워드): 60 => get_rx_packet_size = -127 리턴이 됩니다.
읽기개수(워드):59 : 정상 작동
실험 결과를 추가하였습니다.
RE: W6100 데이타 수신시 -119
by austin ·
getsockopt() 함수 내에서
로 되어 있기 때문에 get_rx_packet_size 값을 datasize_t로 type casting 후에 사용 바랍니다.
해당 문의는 kakaotalk channel로 답변 드렸습니다.