WIZ1000 send data to RS232, but cannot receive nothing
General
No replies yet. Be the first to reply.
Join the discussion.
General
No replies yet. Be the first to reply.
Join the discussion.
Share projects and connect with makers.
Joined before the site update? first.
New to WIZnet Makers?
We sent a verification link to your address. Open it to activate your account, then log in.
Accounts from this email provider are reviewed by an administrator after verification. Approval usually takes one business day.
Already have an account?
Enter your email address. If it belongs to an account, we'll send a link to set a new password. Members who joined before the site update use this to set their password.
If an account uses that address, we sent a link to set a new password. The link works once and expires in 30 minutes.
Know your password?
Need an account?
RE: WIZ1000 send data to RS232, but cannot receive nothing
by Zeljko Hrvoj ·
Solved.
WiZ1000 doesn’t control handshake lines on RS232 connector. And my PLC doesn’t respond back if DTR is not asserted - positive.
What I can measure is that from handshake signals only pin 7 - RTS is active on WIZ1000, and it is always negative voltage. DTR pin 4 is always 0V which means not connected.
I tried WizVSP (connect serial port to remote host - client) to force signal lines and it doesn’t help even if I change the settings on Signal lines tab. My RTS is always low, and DTR is not connected - it’s 0V.
I use external DC voltage to assert DTR high to PLC, so now PLC answers.
RE: RE: WIZ1000 send data to RS232, but cannot receive nothing
by irina WIZnet ·
Great!